    Default 75A breaker for Mecer Inverter - is it necessary?

    I have just invested (?) in a Mecer inverter (https://pclinkshop.co.za/ups-inverte...-ivr-2400lbks/). This will be used for loadshedding - TV, DStv, internet, a few lights etc (nothing really heavy).
    The guide that came with the unit indicates that I should put in a 75A breaker in the positive battery line. The dude at our local electrical place reckons this is not necessary.
    What is the view of the experts out there?
    Triton 3.2 A/T D/Cab 4x4 (EGR blanked, Remapped, 63mm zorst)
    BL Vlooi 295
    Platkar - Rav4
    Previously: Isuzu "LUV", Disco D1 TDi, KZ-TE
    -------------------------------------------------------------------
    A bad day in the bush is better than a good day at the office

  2. #2
    Join Date
    Dec 2015
    Location
    Cape Town
    Age
    47
    Posts
    78
    Thanked: 39

    Default Re: 75A breaker for Mecer Inverter - is it necessary?

    I have a 1500 w inverter and was always a little worried about the breaker so I picked up a 60 amp DC breaker from 4x4 Direct. Just for peace of mind.

  3. #3
    Join Date
    Oct 2009
    Location
    Nelspruit
    Age
    38
    Posts
    904
    Thanked: 977

    Default Re: 75A breaker for Mecer Inverter - is it necessary?

    I dont have one installed. Batteries connected to inverter without a breaker. Use thick cables so that they dont get warm when drawing lots of current. Inverter has protection built in, its actually quite an intelligent piece of equipment for the price.
    20 Ranger Supercab 2.2 auto XLS 4x4
    18 Ranger Double cab Tdci (Swambo)
    12 Conqueror courage

    Dawie van der Merwe
    If you fail to plan, you plan to fail.
    A goal without a plan is just a dream.

  4. #4
    Join Date
    May 2009
    Location
    Hillcrest
    Age
    64
    Posts
    19,435
    Thanked: 8420

    Default Re: 75A breaker for Mecer Inverter - is it necessary?

    Quote Originally Posted by LandyLove View Post
    I dont have one installed. Batteries connected to inverter without a breaker. Use thick cables so that they dont get warm when drawing lots of current. Inverter has protection built in, its actually quite an intelligent piece of equipment for the price.
    Fine, except the fuse or breaker is not there to protect the Inverter, its there to protect the cable and the battery, which the Inverter cant do. Its also there to protect you from fire from the Inverter should the Inverter protection fail. (Inverter protection failing manifests itself as fire.)

    Fuses aren't there for overload, they are there for protection from failures.
    Cheers

    ZS5KAD
    3 Land Rover V8's
    NA - TwinTurbo - SuperCharged
    A V6 and an inline 4

    If you fly or drive to an anti-Fracking meeting, you have no business being there and you wont get my ear......

  5. The Following 5 Users Say Thank You to Fluffy For This Useful Post:


  6. #5
    Join Date
    Oct 2013
    Location
    Centurion
    Age
    64
    Posts
    2,572
    Thanked: 1035

    Default Re: 75A breaker for Mecer Inverter - is it necessary?

    Quote Originally Posted by dust-devil View Post
    I have just invested (?) in a Mecer inverter (https://pclinkshop.co.za/ups-inverte...-ivr-2400lbks/). This will be used for loadshedding - TV, DStv, internet, a few lights etc (nothing really heavy).
    The guide that came with the unit indicates that I should put in a 75A breaker in the positive battery line. The dude at our local electrical place reckons this is not necessary.
    What is the view of the experts out there?
    I would rather use a 100A fuse when using a 2400VA inverter running on 24V.