Home solar setup advise - Page 2
Page 2 of 7 FirstFirst 1 2 3 4 5 6 7 LastLast
Results 21 to 40 of 130
    Thanked: 269
    Default Re: Home solar setup advise
    When I started with this my db was more or less 40 years old - you can imagine what that looks like. Luckily for me, the db is in the garage and I had a 3 row surface mount db installed over the original. This allows me a lot of freedom in moving loads around.
    Row 1:
    Incoming power form municipality through the main switch. Then the Earth leakage distributing power to circuit breakers. Here I have most plugs, the stove and oven, pool pump etc. From this row I then feed my hybrid inverter. 5kVA Axpert.
    Row 2:
    Incoming power from the inverter - whether from 220V straight through the inverter, batteries or solar, passing through another main switch and earth leakage. Then all the loads. In case lights, office power (for computers, wifi etc) and now also the fridge and my borehole pump.
    Row 3:
    A generator switch - but not for a generator - it switches row 2 between the inverter or municipal supply. This way, if my inverter goes down , break or get stolen - I can bypass it safely and get my house back and running with one switch.
    With this setup I can remove a circuit breaker from row one, move it into row 2 and it is immediately on the inverter system. So as I expand my system I can put more load on the inverter. I got 4 x 365 , 48V panels from a friend recently and are now considering to put the pool pump on the inverter and run it only during the day.
    Attachment 558213
    The other day the guy at deltec informed me that my axpert couldnt connect to solar and grid. So its not hybrid as everyone makes it out to be.
    12 Conqueror courage
    17 Ranger Supercab Tdci (Sold)
    97 Defender HCPU Tdi (Sold)
    99 Discovery 2 TD5 GS (Sold)
    Thanked: 269
    Video @ekkekan is referring to
    This is my setup, without the grid tied inverter. What grid tied inverter should I get that doesnt cost more than my existing system? Only then will I add solar to the mix.
    Thanked: 419
    Some time ago I suggested you just add the Solis to your mix. Use the very same Solis as per this video. It cost less than half what your current system cost.
    R7550 for a 3kW Solis and as easy as can be to add to any installation.
    Some comments about the 2 inverter setups vs the Goodwe.
    1. A friend of mine has such a system installed more than a year ago. Just watch the export as it could easily export if a biggish Solis is used. Also pre-paid might switch off with export.
    2. Previous comments were can it work? Greenpro consulting would not advise it if it cannot work.
    3. I doubt that Fluffy would on a regular basis provide the link to this video if it is a scrap way of doing solar.
    In order to use my configuration with the Solis being able to work on a 60-600V input from solar one must just ensure you don't exceed the Axpert PV input with respect to the 150V input limit. This would then mean that the 35-40V panels there can't be more than 3 in series per string.
    As the inverters would just be getting a PV input they will not even know about the 2nd inverter as the Solis would be off line when the grid is off just like it is doing during the night with no PV input.
    Lastly the old style DC type of knife switch use on DC filed coils and main supply to motors means a very cheap method can be use to switch the DC as this switch opens about 40mm between the 2 sources of DC. Never will there be a problem. It is possible that a number of people have never seen these switches. See 6 pictures below.
    If I do miss something with this configuration please lets talk about it so I can also learn about the pot holes with my line of thinking.
    Configuration as per the video but without the actual transfer switch.
    Pics when operating. Cannot load videos - too old to learn
    Just some background to my way of going the 2 inverter route. I started working in an area where a lot of dual contingency is used. One part in operation with a second as stand by. When there is a problem you just switch over to the next and REPAIR the 1st. The current generation seems to be switching over to the stand by and not repairing the 1st. Should the 2nd fail then it is decided which one is less work while the whole system is out of order. Thus using 2 inverters means only half of your functionality is lost when 1 has to be removed to be repaired.
  4. The Following 3 Users Say Thank You to ekkekan For This Useful Post:
  5. #24
    Thanked: 419
    Quote Originally Posted by SchyffS View Post
    Same story, is this what the install looks like?
    From various posts it would be nice if for once and for all clarification to know if your grid tied from the King 1 on the left would be able to supply the 220V from the grid and panels as a proper grid tied would do. Solis in the comments from my side as it is the inverter I have and know a bit about it's operation.
  6. #25
    Sep 2019
    Boksburg
    Thanked: 14
    Also had a hybrid system installed end of Jan this year.
    It dropped my daily consumption from 32kw to about 10kw. It is also upgradeable (parallel mode)
    Does not feed to grid. Have one plug connected to grid only for Pre-paid.
    Also running solar Geyser.
    system for those that is interested:
    1x 5KW 48V Kodak VM III - wide input range
    *fully automatic operation - bi BMS
    1x Battery shelf SABS 800KG
    12x 120AH 12V GEL - German TUV and ISO9001 cert 9
    9x 335 KODAK Pv panels 46VOC - A grade
    20x Meters Silicon 6mm - cost per meter
    1x all connectors & fittings
    1x current specific cable set Inverter & Battery inter connection 35mm2
    1x Solar SUB DB with ALL SAFETY fittings included
    10x Frame length with legs - roof mount - universal flexible
    1x Installation by Ebright/GSS Solar Tech - JHB area
    1x Electrician - GSS recommended contractor, Solar proficient
    2019 Wildtrak 4x4 Bi-Turbo - Current
    2017 Everest 2.2 XLT - Son driving it now
    2016 Ranger 3.2 Manual - Sold
  7. The Following User Says Thank You to Predator For This Useful Post:
  8. #26
    Feb 2008
    Thanked: 1107
    It definitely connects to both.
    Everything is a hammer.
    Unless it is a screw driver.
    Then it it a chisel.
  9. The Following User Says Thank You to Uys For This Useful Post:
  10. #27
    Feb 2008
    Thanked: 1107
    Decided to make a ‘drawing’ of what you explained to be sure I do understand. Please verify:
    Almost, just the small change at the bottom right. The 3rd row selects my supply source to row 2.
  11. The Following User Says Thank You to Uys For This Useful Post:
  12. #28
    Thanked: 269
    Thanks ekkekan, Solis is the word I was looking for. Will certainly be looking into that.
    I cant find a 3kv one for R7550 though. Maybe my bargain hunting skills are a bit off.
  13. The Following User Says Thank You to LandyLove For This Useful Post:
  14. #29
    Thanked: 269
    Would you mind posting a picture of your inverters info display please?
    I was told that you cant connect to grid and solar at the same time, and I cant find the setting for it either. Its either grid, then its basically a UPS. Or its solar, meaning you have to cycle your batteries, also requiring a lot more batteries and solar panels than what I actually need.
  15. The Following User Says Thank You to LandyLove For This Useful Post:
  16. #30
    Feb 2008
    Thanked: 1107
    Sorry man, I am in Malaysia until March.
  17. #31
    Dec 2011
    Cape Town, Grassy Park
    Thanked: 12
    Quote Originally Posted by Predator View Post
    1x5KW 48V Kodak VM III - wide input range
    Hi, does the Kodak VM III mix your energy like a true hybrid?
    Looks like a fantastic system.
  18. #32
    Friemersheim, Southern Cape
    Thanked: 2382
  19. The Following User Says Thank You to Prof For This Useful Post:
  20. #33
    Dec 2011
    Thanked: 12
    Default Home solar setup advise
    This is the method I am also interested in, and the cost can be spread over a period that is manageable.
    Which solis model would this be?
  21. #34
    JHB
    Thanked: 126
    OT
    That explains it. Thought you had developed insomnia
  22. #35
    Thanked: 269
    No problem. March is fine. Im not running out to buy anything just yet.
  23. #36
    Dec 2011
    Thanked: 12
    Hi, every website that I searched for this model (5KW 48V Kodak VM III) says its an OFF-GRID non parralel inverter. Are you sure this inverter can mix energy?
  24. #37
    Dec 2011
    Thanked: 12
    I have come to the conclusion that the Axpert inverters are not hybrid (do not mix energy), none of them (Axpert, Axpert II, KS, MKS, MKS II, VM III & KING).
    To be precise:
    1. They are off-grid
    2. do not mix energy
    3. switches between utility (grid) and PV to meet the load demand, no mixing
    4. charges the batteries
    5. operates as a UPS when there a loss of PV solar and utility (grid).
    Adding a Solis to a setup using anyone of the Axperts could add a 'hybrid' function as the Solis can mix energy. In this instance the Solis will mix utility and PV to meet the demand. Im still not sure which Solis model this is as @ekkekan has not provided the full model name and number yet. Need confirmation about this specific statement.
    Next questions if the above statment is true:
    1. what other inverter combinations are similar to a Solis/Axpert combo?
    2. What additional features would such a combo bring?
    3. And which combo gives you the best value for money? and still cost less than a true hybrid...
    4. Which Axpert model inveretr is best suitable for the Solis/Axpert combo?
    Removing the Solis from the equation and using only an Axpert off-grid inverter:
    5. which Axpert can prioritise supply during the day when the PV power(set as priority) is less then the load to:
    a. continue to provide PV solar to charge the batteries, and
    b. provide utility power to the loads
    6. which Axpert can, during the night (no PV available), set battery as the main supply and switch to utility supply when the battery power is less than the load.
    Or am i getting ahead of myself.
    The Goodwe hybrid can not parralel.....this is a turn off.
  25. The Following User Says Thank You to SchyffS For This Useful Post:
  26. #38
    Thanked: 209
    You need software to do that called ICC with a BMV IF I recall correctly that switches the Axpert back to grid once a certain SOC has been reached.
    What happens when Eskom goes off after the SOC has been reached, I don't know if the Axpert will override the ICC software and start using batteries again.
    Solis + Axpert is a good choice.
    Me, I prefer Victron. Modular, can parallel just like Lego, and it is a true hybrid with some super awesome opensource software.
    Political Correctness is a doctrine, fostered by a delusional, illogical minority, and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a turd by the clean end.
  27. The Following 2 Users Say Thank You to the_terrible_triplett For This Useful Post:
  28. #39
    Thanked: 419
    Sorry for taking so long to answer - one can also google for Solis mini 4G.
    Here one can find information about the Solis true hybrid as an option against the Goodwe. Only 1 model on offer.
    https://www.sustainable.co.za/solis-...dc-switch.html
    Here is the full list of the pure grid tied inverters that meet a good standard.
    https://re-volt.co.za/Store/index.php?route=product/category&path=83_59_67
  29. #40
    Sep 2019
    Boksburg
    Thanked: 14
    Hi here is a diagram of how this inverter operates:
  30. The Following User Says Thank You to Predator For This Useful Post: