Generator FAQ
Results 1 to 2 of 2
Thread: Generator FAQ
    Oct 2006
    CAPE TOWN ,SOUTH AFRICA
    Thanked: 578
    Default Generator FAQ
    • Generator Frequently Asked Questions (FAQ)
    There are so many generators to choose from How do I make up my mind?
    In this age of consumer freedom the choice for many items including generators seems endless, buy in confidence that all our generators are from top Euorpean, American or Japanese companies, we do not sell inferior quality gernerators as sold on auction websites.. Before you choose a generator you may wish to consider the following :
    What size of generator do I require?
    All electrical products have a data plate with information regarding their power usage, for most power tools i.e. drills sanders etc their listed wattage is all the power they require to run. Household items such as central heating pumps, lights, TV's, Video recorders etc. fall in the same catergogry. Items such as freezers, fridges, washing machines, some lawn mowers are normally different, whilst they can state a wattage rating, due to the type of motor they use can require a much greater requirement on start up, when started they then require a smaller usage.
    If you are unsure as to what power usage a product has it is always advisable to contact the relevant manufacturers sales or technical dept, quoting model number and requesting the START UP wattage & RUNNING wattage of your item. With this information you will be able to determine accurately the size of generator you require.
    Do I require a generator that has a long run fuel tank?
    Generators are available in either standard run or long run versions. A standard tank will last for 2-4 hrs, where most long run generators can run through the night, if you are looking to purchase a generator for back up for powercuts then we would recommend a long run tank machine.
    Do I want to run a computer off my generator?
    Running home computers from a standard generator is not advisable, you require a generator that utilises AVR (automatic voltage regulation such as the Briggs Pro Max 6000A or a Inverter such as the Honda EU & EM Range these systems will give you more stable electricity than the mains. Please note: As a generator runs out of fuel, the engine is likely to surge. To avoid this affecting electronic equipment an Uninterruptible Power Supply (UPS) can be used. These are typically sold for use with computers so that data is not lost in the event of a power cut.
    I have bought a generator, and I am concerned about safety. Can I use a personal power breaker?
    The generator is configured differently to the mains supply. The generator has a ‘floating earth’, whilst the mains has an earthed neutral. Whereas it is definitely recommended to use a personal power breaker (RCD) from the mains, for the majority of cases, it is not necessary to use one with a generator. The generators are safe as they are designed.
    Personal power breakers are designed to operate from the mains. If one is to be used with a generator, then it is necessary to modify the generator so that it is configured in the same way as the mains. This is a relatively simple modification for a qualified electrician involving adding a link wire from the neutral terminal to the earth terminal. However, once the generator has been modified, it is necessary to then always use a personal power breaker and to also always use an earth spike, which connects between the generator frame and the ground. Since this is difficult to ensure, it is generally recommended not to modify the generator.
    I have bought a generator, and would like to connect it to my house in case of mains failure. What do I need to do?
    When using a generator as an alternative supply to the mains, there are several precautions that must be observed.
    It is vital that the generator is completely isolated from the mains supply. This ensures that the generator is not attempting to power up the whole neighborhood, but also ensures that it does not electrocute a utility worker trying to restore the mains supply.
    To achieve this, a double-pole, break-before-make, changeover switch must be installed by a qualified electrician.
    This should be fitted between the electricity meter and the building consumer unit. The switch connects the building to either the mains supply or to a lead which can be plugged into the generator.
    Most buildings now have an RCD built into the consumer unit. This is configured to operate from the mains supply with an earthed neutral, and not from a generator with a floating earth. To utilize this protection device, it is necessary to modify the generator so that it is configured in the same way as the mains supply. This is a simple modification for a qualified electrician, involving adding a link wire from the neutral terminal to the earth terminal. It is recommended to make this connection in the plug that is to be used to connect to the generator. This ensures that the generator is unmodified when it is disconnected from the house, and therefore remains safe.
    The plug should be labeled “Do not connect to mains: Neutral-Earth link fitted”. The lead between the generator and the transfer switch is not protected by the RCD, it is therefore recommended to use a steel armored cable for this connection. Finally a local low-impedance earth spike needs to be installed.
    What type of sockets do generators Use?
    Generators for use within the UK use the following sockets. Please not the white 230V 15A Schuko sockets are for European use only.
    What is the difference between kW and kVA? What is power factor?
    There are 3 types of electrical:
    Real Power, measured in Watts (W). This is the power drawn by a resistive load, e.g. a heater element in a kettle, and has a power factor of 1. (unity power factor, cos F=1, 1.0pf or pf=1)
    Reactive Power, measured in Volt Amperes reactive (VAr’s). This is the power drawn by a reactive load (a load with a winding around a core), e.g. an electro-magnet, and has a power factor of 0. (zero power factor, cos F =0, 0pf or pf=0)
    Apparent Power, measured in Volt Amperes (VA). Many loads have a combination of resistive and reactive elements. (in fact it is not possible to produce a purely inductive load, since the wire used to form the windings has a resistance). This combination of elements means that both real power (W) and reactive power (VAr) are drawn together.
    The proportion of Real Power to Reactive Power is defined as the power factor. [Nearly all resistive load (e.g. Universal motor used in hand tools) then power factor 0.95 to 1.0, nearly all inductive load then power factor ~ 0.3]
    The vast majority of single-phase loads have power factors approaching 1. Therefore, single-phase generator power ratings are taken at power factor =1, and are consequently in Watts (W) or kilo Watts (kW), where 1 kW = 1000 W.
    Three-phase loads tend to have lower power factors, approaching 0.8, therefore, three phase generator power ratings are taken at power factor =0.8 and are in VA or kVA.
    There is obviously a relationship between real power, reactive power, apparent power and power factor.
    i) Apparent Power (VA) = Ö [(real power (W))2 + (reactive power (VAr))2]
    And
    ii) Power factor = Real Power (W)
    Apparent Power (VA)
    Therefore…
    Apparent Power (VA) x Power factor = Real power (W)
    If the Power factor =1, then all the Power is real, and
    Apparent Power (VA) = Real Power (W)
    (W = VA @ 1.0 pf)
    For a single-phase generator, the rating should be at 1.0 pf, in which case
    Watts = Volt Amperes.
    But, for a three-phase generator the rating is at 0.8pf.
    This is where confusion can arise!
    Example.
    A three-phase generator has a continuous rating of 5 kVA at 0.8 pf.
    Now, at this rated load, the Real power (kW) will be …
    Real Power (kW) = Apparent Power (kVA) x Power factor
    Real Power = 5 x 0.8 = 4kW
    This means that a generator producing 5kVA at 0.8pf is actually producing 4 kW of Real power, but it is also producing some reactive power.
    From i)…
    5000 VA = Ö [( 4000 W)2 + ( Reactive Power)2]
    Reactive Power = 3000 VAr’s
    It is this combination of 4kW of real power and 3kVAr’s of reactive power that has defined the limit for the generator rating.
    If the same generator was loaded with a resistive load only, then it may be capable of more than 4kW, however, there is no formula that can be used to find this limit from the 0.8pf rating. It can only be found through testing of each machine.
    Similarly, a single-phase generator rated at 4kW, cannot be expected to produce 5kVA at 0.8pf !!!!
    Question: Can I operate sensitive equipment from a generator? Should have AVR
    The output from a portable generator is not as stable as the supply from the mains. The speed of the engine driving the alternator is controlled by a simple mechanical governor; consequently, the speed drops as the load is increased. The frequency of the output voltage is directly dependent on the engine speed; therefore, the frequency of the output varies with load. In addition, the output voltage will vary with load, and with temperature. The output voltage of most standard generators will remain within 230V +/- 10% from no load up to the rated load current quoted on the dataplate. This is the guaranteed range of voltage supplied from the mains utilities.
    The frequency of the output voltage will vary typically from 53Hz at no load to 49Hz at rated load current, whereas the mains supply is unlikely to vary by more than 0.1 Hz.
    Most electronic equipment is designed to cope with these fluctuations and will operate normally. However, it is always recommended to ask the equipment supplier whether their equipment is suitable to be operated from a portable generator.
    Honda Inverter Produces Power Stability
    Computers and power-sensitive testing equipment require what is referred to as "clean power." Clean power is electrical current that is consistent and has a stable "sine wave" or signal. If the lights or other basic appliances in your home were being powered by a generator and there was a fluctuation in the AC power, you’d probably see the lights dim and then return to full brightness—no problem! However, if your computer was being powered by a generator and the voltage fluctuated, chances are the computer would either shut down or at least interrupt the program you were working in.
    In order to overcome this problem, Honda engineers developed a revolutionary form of inverter technology. This process takes the raw power produced by the generator, passes it through a special microprocessor that provides ultra-clean power that boasts a sine wave equal to or better than the current from your household AC wall outlet. This means that, you can operate a computer or laptop direct from a generator.
    ORA
    Ian
    Thanked: 224
    Thanks! Very helpful.
  1. Home Generators
    By NetEddy in forum The 4x4 Pub
    Last Post: 2020/08/31, 10:09 AM
  2. Series II Importing complete wiring loom from the UK
    By Champ in forum Land Rover
    Last Post: 2013/09/25, 02:07 PM
  3. Generators.
    By Andre in forum The 4x4 Pub
    Last Post: 2013/05/29, 08:40 AM
  4. Generators
    By Dave Faddel in forum Camping, Fridges, Accessories
    Last Post: 2009/10/10, 04:31 AM
  5. Generators driving electric motors
    By andre plant in forum Vehicle & Technical Chat - General
    Last Post: 2008/08/24, 11:54 AM