Default Electrician/Electrical Question.


hi,
I'm changing lights in the ceiling. They have used sufix cables.
I have made joins using those black connector blocks.
.
Is that legal from an inspection point of view?

If not - what is correct.
thanks
cc

__________________
Merit before Race - anything else IS Racism.
Stay Calm, engage low-ratio, keep buggering on - a Landy Man
Longevity isn't worth dying for,

Reply With Quote
  #2  
Old 13-10-13, 12:37 PM
hunter26's Avatar
hunter26 hunter26 is offline
Member
 
Join Date: Jan 2012
Location: King Williams Town
Age: 46
Posts: 3,957
Default

Those black connectors are legal>Remember to twist your wire and fold back so your screw catches all strands instead of one strand or the side of the conductor . If heat is present it is best to use screwits as these don't melt. Remember a loose connection causes fire and blown lamps.

__________________
Isuzu STD 2.5d 2x4 rear diffy lock
2x spotlight,2x fog lights
215/80/R15c tyres
1 x great humourous driver
GPS,Bluetooth
Eagle eye dash cam
Craig
I DON'T LIVE IN AFRICA,AFRICA LIVES IN ME- Kyle my son

Reply With Quote
  #3  
Old 13-10-13, 12:47 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

The use of connecting up wires with connectors is legal, bu the connections are to be done in a recognized draw box with a cover.
No open exposed wires are allowed.
For screw in lamps your polarity has to be correct.

If you talking about the wiring in the box on the ceiling where the light fitting is attached to.
If this is the case, yes connectors can be used.

__________________

-------------------------
Ian


Last edited by OFFROAD ADDICT; 13-10-13 at 12:49 PM.
Reply With Quote
  #4  
Old 13-10-13, 02:50 PM
ChrisF's Avatar
ChrisF ChrisF is offline
Member
 
Join Date: Dec 2008
Location: Bellville
Age: 46
Posts: 10,043
Default

Quote:
Originally Posted by Capt Chaos View Post
hi,
I'm changing lights in the ceiling. They have used sufix cables.
I have made joins using those black connector blocks.
.
Is that legal from an inspection point of view?

If not - what is correct.
thanks
cc
since you are asking.


the only "legal way" is to get an electrician to work, AND to issue a COC upon completion.
Reply With Quote
  #5  
Old 13-10-13, 02:57 PM
Woolf Woolf is offline
Member
 
Join Date: Aug 2009
Location: JHB
Age: 60
Posts: 483
Default

I am thinking of changing my 12V downlighters to 220V GU10 LED's. Does this mean every light will need a box?
Reply With Quote
  #6  
Old 13-10-13, 03:04 PM
Muggins Muggins is offline
Member
 
Join Date: Mar 2009
Location: Johannesburg Midrand
Age: 40
Posts: 619
Default

Are they in a normal ceiling as in one can climb into the roof where the lights are?
Reply With Quote
  #7  
Old 13-10-13, 03:08 PM
Genissie's Avatar
Genissie Genissie is offline
Member
 
Join Date: May 2013
Location: Hartenbos
Age: 40
Posts: 326
Default

Quote:
Originally Posted by ChrisF View Post
since you are asking.


the only "legal way" is to get an electrician to work, AND to issue a COC upon completion.
chris, have you seen the "electricians" they send you these days, i ended up fixing after them, never mind how they disrespect your house....

__________________
1992 Toyota Land Cruiser 80, S/W GX 4500 Manual
1994 Toyota Camry 2.2 SEi
2012 Hyundai Santa Fe 3.5 awd

Reply With Quote
  #8  
Old 13-10-13, 03:13 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

Quote:
Originally Posted by Woolf View Post
I am thinking of changing my 12V downlighters to 220V GU10 LED's. Does this mean every light will need a box?
Technically speaking , yes.
But.....the easiest and cost effective way would be to have the one central point in a drawbox, then take a separate 1mm or 1.5mm cable to each light connection. Its easier this way. No exposed wire in the roof space. hehee not that easy. Remember you will require an earth wire (its now 220v) tyhe fitting can be attached to the light fitting (wasnt designed by the brightest of the brightest) , 220v LED lamps are metal and the metal makes contact with the fitting, so thats where the earth is required. ALL steel fittings must be earthed....

__________________

-------------------------
Ian

Reply With Quote
  #9  
Old 13-10-13, 03:29 PM
ChrisF's Avatar
ChrisF ChrisF is offline
Member
 
Join Date: Dec 2008
Location: Bellville
Age: 46
Posts: 10,043
Default

Quote:
Originally Posted by Genissie View Post
chris, have you seen the "electricians" they send you these days, i ended up fixing after them, never mind how they disrespect your house....
I KNOW ...


Fortunately I DO have the training, and friend that can sign off.
Reply With Quote
  #10  
Old 13-10-13, 07:23 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

your friend is stupid,
Reply With Quote
  #11  
Old 13-10-13, 07:28 PM
Errol's Avatar
Errol Errol is offline
Member
 
Join Date: Jan 2011
Location: Port Elizabeth
Age: 59
Posts: 901
Default

Quote:
Originally Posted by OFFROAD ADDICT View Post
your friend is stupid,
+1

__________________


2014 Kia Sportage 2.0 Auto

2009 Ford Ranger 3.0 XLT TDCI 4X4 Super Cab

Reply With Quote
  #12  
Old 13-10-13, 07:47 PM
Jaws. Jaws. is offline
Member
 
Join Date: May 2009
Location: JHB
Age: 35
Posts: 1,405
Default

Quote:
Originally Posted by OFFROAD ADDICT View Post
your friend is stupid,
??
Reply With Quote
  #13  
Old 13-10-13, 08:53 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

Quote:
Originally Posted by ChrisF View Post
I KNOW ...


Fortunately I DO have the training, and friend that can sign off.
Chris, i know you are stirring now

__________________

-------------------------
Ian

Reply With Quote
  #14  
Old 14-10-13, 07:36 AM
hunter26's Avatar
hunter26 hunter26 is offline
Member
 
Join Date: Jan 2012
Location: King Williams Town
Age: 46
Posts: 3,957
Default

Quote:
Originally Posted by ChrisF View Post
I KNOW ...


Fortunately I DO have the training, and friend that can sign off.

Chris are u an Electrician or Lectrician ie qualified or not

Craig

__________________
Isuzu STD 2.5d 2x4 rear diffy lock
2x spotlight,2x fog lights
215/80/R15c tyres
1 x great humourous driver
GPS,Bluetooth
Eagle eye dash cam
Craig
I DON'T LIVE IN AFRICA,AFRICA LIVES IN ME- Kyle my son

Reply With Quote
  #15  
Old 14-10-13, 07:37 AM
hunter26's Avatar
hunter26 hunter26 is offline
Member
 
Join Date: Jan 2012
Location: King Williams Town
Age: 46
Posts: 3,957
Default

Quote:
Originally Posted by OFFROAD ADDICT View Post
Technically speaking , yes.
But.....the easiest and cost effective way would be to have the one central point in a drawbox, then take a separate 1mm or 1.5mm cable to each light connection. Its easier this way. No exposed wire in the roof space. hehee not that easy. Remember you will require an earth wire (its now 220v) tyhe fitting can be attached to the light fitting (wasnt designed by the brightest of the brightest) , 220v LED lamps are metal and the metal makes contact with the fitting, so thats where the earth is required. ALL steel fittings must be earthed....
1.5 mm for lights is recommended.


Craig

__________________
Isuzu STD 2.5d 2x4 rear diffy lock
2x spotlight,2x fog lights
215/80/R15c tyres
1 x great humourous driver
GPS,Bluetooth
Eagle eye dash cam
Craig
I DON'T LIVE IN AFRICA,AFRICA LIVES IN ME- Kyle my son

Reply With Quote
  #16  
Old 14-10-13, 07:43 AM
WillysCJ's Avatar
WillysCJ WillysCJ is online now
Member
 
Join Date: Apr 2013
Location: Witbank
Age: 31
Posts: 2,741
Default

Here is the standard. (I feel like Apoc, pasting the law)

6.3.6.1
The cables may be installed
a) on the surface,
b) under plaster,
c) under a raised floor,
d) in hollows (such as in walls and partitions) (no additional protection
being needed),
e) in roof spaces,
f) direct in the ground (see 6.4.4.2, unarmoured buried cables),
g) outdoors or exposed to water (but unless the manufacturer proves
that the cables can withstand ultraviolet radiation, the cable shall be
out of sight of the sky), and
h) under screed if protected by an earth leakage protection device with a
rated earth leakage tripping current (rated residual current)
IΔn not
exceeding 30 mA.
Amdt 5

6.3.6.2
These cables shall not be buried direct in concrete.

Amdt 3; amdt 5
6.3.7 Joints and terminations
6.3.7.1
Joints and terminations of cables, cores and conductors shall be
made in accordance with manufacturers' instructions or the
appropriate part of SANS 10198. Flexible cables shall only be joined

using termination boxes, cable couplers or manufacturers’ jointing kits. All
with 5.1.1, except for joints made and sealed permanently and intended
to be maintenance free.
Amdt 1; amdt 3; amdt 4; amdt 5

6.3.7.2
Joints and terminations shall not
a) adversely affect the current-carrying capacity, the insulation resistance
or the earth continuity of the cable, core or conductor in which
they are made,
b) be made in any connector, bend, elbow or tee-piece of a conduit,
c) allow the strands of a stranded conductor to spread, or
d) require strands of a stranded conductor to be cut away to allow
connection of the conductors (for example, to terminals).

6.3.7.3
Any armouring or sheathing shall be terminated in or on
equipment. Armour wires shall be terminated by a clamp or gland in such
a way that
a) pressure is not applied to insulating material, and
b) there is an earth tag washer (or similar) for connecting to the earth

continuity conductor.

__________________
Gerhard
-------------------------------------------------------


2014 Jeep Wrangler Unlimited CRD AUTO
2011 Nissan Qashqai 2.0 diesel (SWAMBO)

Reply With Quote
  #17  
Old 14-10-13, 06:20 PM
ChrisF's Avatar
ChrisF ChrisF is offline
Member
 
Join Date: Dec 2008
Location: Bellville
Age: 46
Posts: 10,043
Default

Quote:
Originally Posted by hunter26 View Post
Chris are u an Electrician or Lectrician ie qualified or not

Craig
in accordance with the current legislation I have the required training and experience to "work under the supervision of an electrician". Thus I may legally do the basic work, and have it signed off.


in simple language - if I go and do my wiremans pratical exam now I could do all this work and sign it off myself.


the remnants of multi skilled practical training during my years as an appy.




ORA soek jy n appy ??
Reply With Quote
  #18  
Old 14-10-13, 06:33 PM
dylanhofmann's Avatar
dylanhofmann dylanhofmann is offline
Member
 
Join Date: Sep 2013
Location: muzenburg capetown
Age: 34
Posts: 20
Default

by sans 10142 all wiring that is new must be in conduit, (no body ever does it )
if existing wiring all connections must be made in round or some form of sabs approved connection box
to be safe and have a good electrical bonding rather use ferrules
every thing that you do must be earthed, always even if it is required or not.

cheep gets what cheep pays for .
there are no short cuts in electricity. that equals a shock or death. you choose

some more stuff but im still learning too, and i never stop learning , and that's how it should be

dylan
Reply With Quote
  #19  
Old 14-10-13, 06:33 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

Quote:
Originally Posted by ChrisF View Post
in accordance with the current legislation I have the required training and experience to "work under the supervision of an electrician". Thus I may legally do the basic work, and have it signed off.


in simple language - if I go and do my wiremans pratical exam now I could do all this work and sign it off myself.


the remnants of multi skilled practical training during my years as an appy.




ORA soek jy n appy ??
Ek soek professional manne mense wat kan Practical spell
Working under supervision, what does that mean,

I dont really ask who or what did the job, the guy that signs it off, its his name on the COC, He takes the wrap.

__________________

-------------------------
Ian

Reply With Quote
  #20  
Old 14-10-13, 06:34 PM
ChrisF's Avatar
ChrisF ChrisF is offline
Member
 
Join Date: Dec 2008
Location: Bellville
Age: 46
Posts: 10,043
Default

Quote:
Originally Posted by OFFROAD ADDICT View Post
your friend is stupid,
arent those the best ones ....







ORA he walks over, we discuss the projecct, he supplies all the materials, I fit it, he inspects, I close, he signs off. NICE
Reply With Quote
  #21  
Old 14-10-13, 06:39 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

Quote:
Originally Posted by ChrisF View Post
arent those the best ones ....







ORA he walks over, we discuss the projecct, he supplies all the materials, I fit it, he inspects, I close, he signs off. NICE
I dont sign other peoples jobs off, it can come back to haunt me later, if there was something he did that i didnt see.

__________________

-------------------------
Ian

Reply With Quote
  #22  
Old 14-10-13, 06:43 PM
ChrisF's Avatar
ChrisF ChrisF is offline
Member
 
Join Date: Dec 2008
Location: Bellville
Age: 46
Posts: 10,043
Default

sien dom pels is beter as bang pels ....


jokes aside - signing off another persons work is VERY risky business !!
Reply With Quote
  #23  
Old 16-10-13, 08:24 AM
hunter26's Avatar
hunter26 hunter26 is offline
Member
 
Join Date: Jan 2012
Location: King Williams Town
Age: 46
Posts: 3,957
Default

Quote:
Originally Posted by OFFROAD ADDICT View Post
Ek soek professional manne mense wat kan Practical spell
Working under supervision, what does that mean,

I dont really ask who or what did the job, the guy that signs it off, its his name on the COC, He takes the wrap.

Hi Chris,if you are not a qualified electrician but been in the trade for years,then go do your single phase license,it saves u from paying someone else.Unfortunately 3ph can only be obtained if qualified.Here we have many unqualified that wire houses but someone else does the COC.The problem with taking Joe street's COC is if something happens and u take action against the person who signed,9/10 he has nothing u can sue him for.Advice,employ an electrician who is registered with the contracting board,contracting associations,dept of labor.

Craig

__________________
Isuzu STD 2.5d 2x4 rear diffy lock
2x spotlight,2x fog lights
215/80/R15c tyres
1 x great humourous driver
GPS,Bluetooth
Eagle eye dash cam
Craig
I DON'T LIVE IN AFRICA,AFRICA LIVES IN ME- Kyle my son

Reply With Quote
  #24  
Old 16-10-13, 09:54 AM
ChrisF's Avatar
ChrisF ChrisF is offline
Member
 
Join Date: Dec 2008
Location: Bellville
Age: 46
Posts: 10,043
Default

Quote:
Originally Posted by hunter26 View Post
Hi Chris,if you are not a qualified electrician but been in the trade for years,then go do your single phase license,it saves u from paying someone else.Unfortunately 3ph can only be obtained if qualified.Here we have many unqualified that wire houses but someone else does the COC.The problem with taking Joe street's COC is if something happens and u take action against the person who signed,9/10 he has nothing u can sue him for.Advice,employ an electrician who is registered with the contracting board,contracting associations,dept of labor.

Craig
If I stayed on the tools 3 months longer I would have done the wiremans test.


But life takes strange turns with us.


Since then I did my engineering degree and "Government ticket". So now I only do the odd job at home - when I want a break from all the paper work ..
Reply With Quote
  #25  
Old 16-10-13, 12:08 PM
OFFROAD ADDICT's Avatar
OFFROAD ADDICT OFFROAD ADDICT is online now
ORA
 
Join Date: Oct 2006
Location: False Bay ,Cape Town
Age: 64
Posts: 13,106
Default

ChrisF, I will swop jobs anytime
Reply With Quote
  #26  
Old 16-10-13, 01:27 PM
hunter26's Avatar
hunter26 hunter26 is offline
Member
 
Join Date: Jan 2012
Location: King Williams Town
Age: 46
Posts: 3,957
Default

Quote:
Originally Posted by ChrisF View Post
If I stayed on the tools 3 months longer I would have done the wiremans test.





But life takes strange turns with us.





Since then I did my engineering degree and "Government ticket". So now I only do the odd job at home - when I want a break from all the paper work ..
Great, I may bother you with some Technical Elect questions in the future if that's okay.


Craig

__________________
Isuzu STD 2.5d 2x4 rear diffy lock
2x spotlight,2x fog lights
215/80/R15c tyres
1 x great humourous driver
GPS,Bluetooth
Eagle eye dash cam
Craig
I DON'T LIVE IN AFRICA,AFRICA LIVES IN ME- Kyle my son

Reply With Quote
  #27  
Old 16-10-13, 01:56 PM
petermoffat's Avatar
petermoffat petermoffat is offline
Member
 
Join Date: Aug 2009
Location: Ladysmith
Age: 32
Posts: 2,695
Default

Quote:
Originally Posted by OFFROAD ADDICT View Post
ChrisF, I will swop jobs anytime
I don't know that that's a good deal for you.. It would be nice to have a jobs in a trade where I work every day, then go home and don't think about it. Your hands can be idle when you put your tools down, but you mind is harder to switch off..

Electricians and engineers are opposite sides of a coin, and you need both, but I sometimes wonder if the sparkies didn't get the good side

__________________
Office Johnny

2008 Triton CC 3.5V6 4x2 - Sold
2007 Triton DC 2.5DiD 4x4 - Sold



Reply With Quote
  #28  
Old 16-10-13, 06:43 PM
Genissie's Avatar
Genissie Genissie is offline
Member
 
Join Date: May 2013
Location: Hartenbos
Age: 40
Posts: 326
Default

ek verwonder net wie teken alles af in ons buurtes wat so deur die res van ons gesponsor word, daar waar elkeen sommer so van die straat pale af "tap"

__________________
1992 Toyota Land Cruiser 80, S/W GX 4500 Manual
1994 Toyota Camry 2.2 SEi
2012 Hyundai Santa Fe 3.5 awd

Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question for the IT networking gurus SimonB The 4x4 Pub 4 05-02-10 02:59 PM
Question on fixtures when moving house! JPMaraisZA The 4x4 Pub 12 01-02-10 03:37 PM
Question about 3.5V6 LWB Gav3.5V6 Mitsubishi 9 25-01-10 12:59 PM
Very Dumb Question Re TD 5 Defender 110 Transfer Box Oil Plug EVH Land Rover 6 07-01-10 09:10 AM
Question for the Fundis paramedicmoz Land Rover 1 04-10-09 08:29 PM




All times are GMT +2. The time now is 08:52 PM.

Disclaimer and Terms of Service

Imvo Trading Solutions CC t/a 4x4Community.
PO Box 29132, Sunridge Park, Port Elizabeth, 6008, South Africa


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2014, vBulletin Solutions, Inc.